Heat Exchanger LMTD

Under steady flow with constant UU and specific heats, heat exchanger duty is
q=UAΔTlmFq=UA\,\Delta T_{\mathrm{lm}}\,F
where
ΔTlm\Delta T_{\mathrm{lm}}
is the log-mean temperature difference. For counterflow
ΔTlm=(ΔTaΔTb)/ln(ΔTa/ΔTb)\Delta T_{\mathrm{lm}}=(\Delta T_a-\Delta T_b)/\ln(\Delta T_a/\Delta T_b)
; cross/shell-and-tube use correction FF (RC Sachdeva / GATE HT).

Key formulas & points

Skim these first — then read the full notes below.

  • Energy balance: q=m˙hcp,h(Th,iTh,o)=m˙ccp,c(Tc,oTc,i)q=\dot{m}_h c_{p,h}(T_{h,i}-T_{h,o})=\dot{m}_c c_{p,c}(T_{c,o}-T_{c,i}).
  • Rate equation: q=UAΔTlmq=UA\Delta T_{\mathrm{lm}} (counter/parallel with proper end ΔT).
  • LMTD: ΔTlm=ΔTaΔTbln(ΔTa/ΔTb)\Delta T_{\mathrm{lm}}=\dfrac{\Delta T_a-\Delta T_b}{\ln(\Delta T_a/\Delta T_b)}.
  • Counterflow: usually larger LMTD than parallel for same terminal temperatures.
  • Shell-and-tube / crossflow: q=UAFΔTlm,cfq=UA\,F\,\Delta T_{\mathrm{lm,cf}} with FF from charts (F0.75F\gtrsim 0.75 preferred).
  • Overall UU: 1UA=R\dfrac{1}{UA}=\sum R including films, wall, fouling.
  • NTU–effectiveness is alternative when outlet temperatures are unknown.

Topic details

Definition and physical meaning

A heat exchanger transfers heat between two fluids without mixing (in recuperators). The LMTD method sizes or rates an exchanger when inlet/outlet temperatures are known (or assumed).
Log-mean temperature difference
ΔTlm=ΔTaΔTbln(ΔTa/ΔTb)\Delta T_{\mathrm{lm}}=\frac{\Delta T_a-\Delta T_b}{\ln(\Delta T_a/\Delta T_b)}

where ΔTa\Delta T_a and ΔTb\Delta T_b are the temperature differences between hot and cold fluids at the two ends of the exchanger.
Heat transfer rate
q=UAΔTlmq=UA\,\Delta T_{\mathrm{lm}}

(for pure parallel or counterflow). For more complex flow arrangements:
q=UAFΔTlm,cfq=UA\,F\,\Delta T_{\mathrm{lm,cf}}

with ΔTlm,cf\Delta T_{\mathrm{lm,cf}} based on counterflow end differences and F1F\le 1 a configuration correction factor.
Physical parameters
Symbol
Meaning
SI unit
qq
Heat transfer rate
W\mathrm{W}
UU
Overall heat-transfer coeff.
W/(m2K)\mathrm{W/(m^2\cdot K)}
AA
Heat-transfer area
m2\mathrm{m^2}
ΔTlm\Delta T_{\mathrm{lm}}
Log-mean temp. difference
K\mathrm{K}
FF
LMTD correction factor
m˙\dot{m}
Mass flow rate
kg/s\mathrm{kg/s}
cpc_{p}
Specific heat
J/(kgK)\mathrm{J/(kg\cdot K)}
Th,i,Th,oT_{h,i},T_{h,o}
Hot in / out
K\mathrm{K} or °C
Tc,i,Tc,oT_{c,i},T_{c,o}
Cold in / out
K\mathrm{K} or °C
Hot fluid →← Cold fluid
Fig — Shell-and-tube counter-flow (schematic)

Schematic diagram for study — aligned with standard B.Tech / GATE syllabus.

Counter-flow heat exchanger. LMTD method — RC Sachdeva / standard heat transfer texts used in Indian universities.

Core assumptions (LMTD method)

1. Steady flow and heat transfer.
2. Negligible heat loss to surroundings (well insulated).
3. Negligible kinetic/potential energy changes; PE/KE ignored in energy balance.
4. Constant specific heats cpc_{p} (or use mean values).
5. Constant overall coefficient UU along the exchanger (or suitable average).
6. Single-phase fluids (or isothermal phase-change on one side — then LMTD still applies with care).
7. No axial conduction in the wall that smears the ΔT profile excessively.
If UU or cpc_{p} vary strongly, integrate locally or use numerical methods / ε–NTU with care.

Energy balance and end temperature differences

Capacity rates: Ch=m˙hcp,hC_h=\dot{m}_h c_{p,h}, Cc=m˙ccp,cC_c=\dot{m}_c c_{p,c}.

Formulas (Indian textbook notation)

  • q=Ch(Th,iTh,o)=Cc(Tc,oTc,i)q = C_{h}(T_{h,i}-T_{h,o}) = C_{c}(T_{c,o}-T_{c,i})
Parallel flow (both fluids enter at same end):
ΔTa=Th,iTc,i,ΔTb=Th,oTc,o\Delta T_a=T_{h,i}-T_{c,i},\qquad\Delta T_b=T_{h,o}-T_{c,o}
Counterflow (fluids enter at opposite ends):
ΔTa=Th,iTc,o,ΔTb=Th,oTc,i\Delta T_a=T_{h,i}-T_{c,o},\qquad\Delta T_b=T_{h,o}-T_{c,i}
Why log-mean? Local dq=U(ThTc)dAdq = U(T_{h}-T_{c})dA. With linear relation between ΔT\Delta T and qq from energy balances, integrating yields LMTD — not the arithmetic mean (ΔTa+ΔTb)/2(\Delta T_a+\Delta T_b)/2, except when ΔTaΔTb\Delta T_a\approx\Delta T_b.

Overall U and fouling

For a plane wall or thin tube (approximate):
1U=1hi+Rf,i+tk+Rf,o+1ho\frac{1}{U}=\frac{1}{h_i}+R_{f,i}+\frac{t}{k}+R_{f,o}+\frac{1}{h_o}

(area basis must be consistent — UiAi=UoAoU_{i} A_{i} = U_{o} A_{o}).
Fouling factors RfR_{f} account for scale/deposits; design UU is lower than clean UU.
Shell-and-tube: use FF charts with parameters
P=Tt,oTt,iTs,iTt,i,R=Ts,iTs,oTt,oTt,iP=\frac{T_{t,o}-T_{t,i}}{T_{s,i}-T_{t,i}},\qquad R=\frac{T_{s,i}-T_{s,o}}{T_{t,o}-T_{t,i}}

(tube and shell fluid temperatures). Avoid designs with F<0.75F<0.75 (temperature-cross sensitivity).

Counterflow vs parallel flow

For the same four terminal temperatures, counterflow LMTD \ge parallel-flow LMTD, so required A=q/(ULMTD)A=q/(U\,\mathrm{LMTD}) is smaller for counterflow.
Counterflow can also achieve Tc,o>Th,oT_{c,o}>T_{h,o} (cold outlet hotter than hot outlet) — impossible in simple parallel flow without violating second-law ΔT direction along the device.
Special case: if one fluid is isothermal (evaporation/condensation), parallel and counterflow LMTD expressions coincide.

Step-by-step problem approach

1. Sketch flow arrangement; label all four terminal temperatures.
2. From energy balance, find unknown outlet (if one unknown) using q=CΔTq=C\Delta T.
3. Form ΔTa\Delta T_a, ΔTb\Delta T_b for parallel or counterflow.
4. Compute
ΔTlm=(ΔTaΔTb)/ln(ΔTa/ΔTb)\Delta T_{\mathrm{lm}}=(\Delta T_a-\Delta T_b)/\ln(\Delta T_a/\Delta T_b)
.
5. q=UAΔTlmq=UA\Delta T_{\mathrm{lm}} (or include FF).
6. If sizing: A=q/(UFΔTlm)A=q/(U F\Delta T_{\mathrm{lm}}).
7. Check ΔTa\Delta T_a and ΔTb\Delta T_b same sign and nonzero; if equal, LMTD = that value.
8. Units: °C differences equal Kelvin differences.

Common mistakes in exams

• Using arithmetic mean (ΔTa+ΔTb)/2(\Delta T_a+\Delta T_b)/2 instead of LMTD.
• Swapping parallel vs counterflow end pairings.
• Applying F=1F = 1 to multipass shell-and-tube without checking charts.
• Mixing UU based on inner area with outer area AA.
• Allowing a temperature cross in parallel-flow calculations.
• Forgetting fouling when computing design UU.

Worked examples

Try the problem first — open the solution when you are ready to check.

Counterflow LMTD and area

Problem

Hot oil cools from Th,i=120CT_{h,i}=120^\circ\mathrm{C} to Th,o=80CT_{h,o}=80^\circ\mathrm{C}. Cold water heats from Tc,i=30CT_{c,i}=30^\circ\mathrm{C} to Tc,o=50CT_{c,o}=50^\circ\mathrm{C}. q=50kWq=50\,\mathrm{kW}, U=400W/(m2K)U=400\,\mathrm{W/(m^2\cdot K)}. Find LMTD (counterflow) and required AA.

Solution

Formulas (Indian textbook notation)

  • ΔTa=Th,iTc,o=12050=70K\Delta T_a=T_{h,i}-T_{c,o}=120-50=70\,\mathrm{K}

Formulas (Indian textbook notation)

  • ΔTb=Th,oTc,i=8030=50K\Delta T_b=T_{h,o}-T_{c,i}=80-30=50\,\mathrm{K}

Formulas (Indian textbook notation)

  • ΔTlm=7050ln(70/50)=20ln(1.4)=59.44K\Delta T_{\mathrm{lm}}=\frac{70-50}{\ln(70/50)}=\frac{20}{\ln(1.4)}=59.44\,\mathrm{K}

Formulas (Indian textbook notation)

  • A=qUΔTlm=50000400×59.44=2.103m2A=\frac{q}{U\Delta T_{\mathrm{lm}}}=\frac{50000}{400\times 59.44}=2.103\,\mathrm{m^2}

Parallel vs counterflow LMTD

Problem

Same terminal temperatures as above. Compute parallel-flow LMTD and compare.

Find outlet from energy balance then LMTD

Problem

Hot fluid: m˙h=0.5kg/s\dot{m}_h=0.5\,\mathrm{kg/s}, cp,h=2.0kJ/(kgK)c_{p,h}=2.0\,\mathrm{kJ/(kg\cdot K)}, Th,i=150CT_{h,i}=150^\circ\mathrm{C}. Cold: m˙c=0.8kg/s\dot{m}_c=0.8\,\mathrm{kg/s}, cp,c=4.18kJ/(kgK)c_{p,c}=4.18\,\mathrm{kJ/(kg\cdot K)}, Tc,i=25CT_{c,i}=25^\circ\mathrm{C}, Tc,o=45CT_{c,o}=45^\circ\mathrm{C}. Counterflow, U=500W/(m2K)U=500\,\mathrm{W/(m^2\cdot K)}. Find AA.

Practice questions

Most-asked interview and GATE questions for this topic — expand any item for a model answer.

  1. 1
    What is LMTD? Write its expression for a double-pipe exchanger.

    Model answer

    Log Mean Temperature Difference: LMTD=ΔT1ΔT2ln(ΔT1/ΔT2)\mathrm{LMTD}=\dfrac{\Delta T_1-\Delta T_2}{\ln(\Delta T_1/\Delta T_2)} where ΔT1,ΔT2\Delta T_1,\Delta T_2 are the temperature differences between hot and cold fluids at the two ends.
  2. 2
    Why use log mean rather than arithmetic mean ΔT\Delta T?

    Model answer

    Local ΔT\Delta T varies exponentially along the exchanger when UU and capacities are constant. Integrating dq=UdAΔTdq=U\,dA\,\Delta T yields the log mean, not the arithmetic mean.
  3. 3
    Write the heat transfer rate using LMTD.

    Model answer

    q=UALMTDq=UA\,\mathrm{LMTD} for pure counterflow or parallel flow (with appropriate end ΔT\Delta Ts). UU is the overall heat transfer coefficient.
  4. 4
    Define ΔT1\Delta T_1 and ΔT2\Delta T_2 for parallel flow and counterflow.

    Model answer

    Parallel: ΔT1=Th,inTc,in\Delta T_1=T_{h,\mathrm{in}}-T_{c,\mathrm{in}}, ΔT2=Th,outTc,out\Delta T_2=T_{h,\mathrm{out}}-T_{c,\mathrm{out}}. Counterflow: ΔT1=Th,inTc,out\Delta T_1=T_{h,\mathrm{in}}-T_{c,\mathrm{out}}, ΔT2=Th,outTc,in\Delta T_2=T_{h,\mathrm{out}}-T_{c,\mathrm{in}}.
  5. 5
    Which arrangement gives higher LMTD for the same terminal temperatures — parallel or counterflow?

    Model answer

    Counterflow generally gives a larger LMTD (and can achieve closer temperature approaches). Parallel flow LMTD is smaller; cold fluid cannot exceed hot outlet in the ideal limit.
  6. 6
    What is the LMTD correction factor FF?

    Model answer

    For shell-and-tube, crossflow, and multipass exchangers, q=UAFLMTDcfq=UAF\,\mathrm{LMTD}_{\mathrm{cf}} where LMTDcf\mathrm{LMTD}_{\mathrm{cf}} is computed as if counterflow and F1F\le 1 from charts using PP and RR.
  7. 7
    Define temperature effectiveness PP and capacity ratio RR used in FF charts.

    Model answer

    P=t2t1T1t1P=\dfrac{t_2-t_1}{T_1-t_1} (tube-side rise over inlet difference), R=T1T2t2t1R=\dfrac{T_1-T_2}{t_2-t_1} (shell drop over tube rise). Notation varies by textbook; follow the chart’s definitions.
  8. 8
    When is LMTD equal to the arithmetic mean temperature difference?

    Model answer

    When ΔT1=ΔT2\Delta T_1=\Delta T_2 (balanced counterflow with equal capacity rates, or condensers/evaporators with one fluid isothermal in a way that end differences match). Then LMTD=ΔTam\mathrm{LMTD}=\Delta T_{\mathrm{am}}.
  9. 9
    How do you treat a condenser or evaporator in LMTD analysis?

    Model answer

    One fluid stays at saturation temperature. End differences use that constant TsatT_{\mathrm{sat}}. Energy balance: q=m˙hfgq=\dot{m}h_{fg} (phase change) equals m˙cpΔT\dot{m}c_p\Delta T of the single-phase stream.
  10. 10
    State assumptions behind the classical LMTD derivation.

    Model answer

    Steady flow; constant UU; constant specific heats (or use enthalpy); negligible heat loss to surroundings; single-pass pure parallel/counterflow; kinetic/potential changes neglected; no axial conduction in fluids.
  11. 11
    Compare LMTD and NTU–effectiveness methods — when is each convenient?

    Model answer

    LMTD: when all four terminal temperatures (or enough to get both end ΔT\Delta Ts) are known — sizing AA. NTU–ε\varepsilon: when outlet temperatures are unknown — rating problems with known UAUA and inlet conditions.
  12. 12
    What happens to required area if LMTD decreases for fixed qq and UU?

    Model answer

    From q=UALMTDq=UA\,\mathrm{LMTD}, A=q/(ULMTD)A=q/(U\,\mathrm{LMTD}) rises — closer temperature approaches need more area.
  13. 13
    Can cold fluid exit hotter than hot fluid exit in counterflow? In parallel flow?

    Model answer

    Counterflow: yes, possible (temperature cross of exit streams). Parallel flow: no — cold outlet cannot exceed hot outlet for the same exchanger.
  14. 14
    How is fouling incorporated with LMTD design?

    Model answer

    Fouling factors add to 1U\frac{1}{U}: 1/Uo=1/ho+Rf,o++Rwall+Rf,i(Ao/Ai)+1/U_o=1/h_o+R_{f,o}+\cdots+R_{\mathrm{wall}}+R_{f,i}(A_o/A_i)+\cdots. Design UU is lower than clean UU, increasing required AA.
  15. 15
    If ΔT1\Delta T_1 and ΔT2\Delta T_2 differ greatly, why is arithmetic mean unsafe?

    Model answer

    Arithmetic mean overpredicts the effective driving force when ΔT1/ΔT2\Delta T_1/\Delta T_2 is large, underestimating required area. Always use LMTD (or FLMTDF\cdot\mathrm{LMTD}).

Exams & GATE

  • 1
    Textbook: RC Sachdeva (heat exchangers); Incropera Ch. 11.
  • 2
    Never average end temperature differences arithmetically when ΔT\Delta T varies — use LMTD.
  • 3
    GATE favourites: counter vs parallel comparison, FF correction concept, and fouling factors in UU.

📖 Standard books (India)

  • Fundamentals of Engineering Heat & Mass TransferRC Sachdeva

    Read: Ch. 11–12

    Heat transfer and heat exchangers